String Configuration |
Configuration by Strings of I/O Tags is performed using the Device and Item fields of each Tag.
That new configuration method does not work with Elipse SCADA, which still uses the old numerical configuration, with N and B parameters.
N and B parameters are not used when configuring by Strings and they must be kept in 0 (zero).
Configuration by Strings makes Tag configuration more readable, making it easy to configure and maintain applications.
Tags configured by Strings can be simple Tags or Block Tags, in which their Device and Item fields with the same syntax.
In the Device field, the Slave Id, or a device's identification address, must be provided as a number between 0 (zero) and 255 followed by a colon, such as "1:", "101:", or "225:".
Please remember that, in Modbus RTU Serial protocol, the Slave Id "0" (zero) is reserved for broadcasting, which only makes sense if used for writing operations, because there is no return from devices, or else conflicts may happen.
Optionally, the Slave Id may appear at the beginning of the Item field, explained later, and in this case the Device field must be kept empty. This option is detailed next.
The Item field must provide all addressing and operation information to be performed by a Tag, using the next syntax, in which parameters between brackets are optional.
<addressing space><address>[.<type>[<size of type>]][.<byte order>][/bit]
As mentioned earlier, users can alternatively provide a Slave Id at the beginning of the Item field, according to the next example.
<slave id>:<addressing space><address>[.<type>[<size of type>]][.<byte order>][/bit]
In this case, as already explained, users must keep the Device field empty.
The next examples show the most common usage cases. Notice that quotation marks must not be added to an application.
1.Reading or writing Holding Registers, functions 03 and 16, on address 100 of a device with Slave Id 1 (one), and Slave Id provided in the Device field:
a.Device: "1:"
b.Item: "hr100"
2.Reading or writing Holding Registers, functions 03 and 16, on address 120 of a device with Slave Id 3 (three), and Slave Id provided in the Item field:
a.Device: "" (empty String)
b.Item: "3:hr120"
3.Reading or writing Coils, functions 01 and 15, on address 65535 (FFFFh) of a device with Slave Id 4 (four), here provided in the Item field:
b.Item: "4:cl&hFFFF" (or optionally "4:cl65535")
The next figure shows examples of String-configured Tags in Elipse E3, in Elipse Power, or in Elipse Water.
Mandatory fields for all Tags are described next and individually detailed later in this topic:
1.Addressing space: A mnemonic defining a set of protocol's reading and writing functions to use. For more information, please check the table with all supported mnemonics later on this topic.
2.Address: A numerical value identifying an item's address, register or bit, to read or write within the defined addressing space. These values can be provided in decimal, hexadecimal, or octal. For decimal values, no prefix is needed, or optionally a "&d" prefix can be used. For hexadecimal values, use the "&h" prefix, such as "&hFFFF". For octal values, use the "&o" prefix, such as "&o843". This address can have an offset relative to the address effectively sent in a communication frame, which depends on the convention used by the manufacturer. When in doubt about addressing conventions, please check topic Addressing Tips (Modbus Convention). Particularly, check whether a device implements the default offset of protocol's Data Model. Please check the Data Address Model Offset option on the Modbus tab.
The next fields are optional, used for extensions to the default protocol or for compatibility with devices not fully compliant with the protocol, and they are also individually detailed later in this topic:
1.Type: Defines how bytes from the data area of a communication frame must be interpreted. If omitted, the default types of the protocol for the respective functions are used, that is, Word for functions to access registers and Bit for functions to access digital data, Coils and Discrete Inputs. Please check the mnemonics table for all supported types later in this topic.
2.Size of type: Users must specify this field only for variable-size types, such as BCD and String. Its numerical value indicates the size of a data type in bytes.
3.Byte order: Mnemonic indicating the byte order of numerical values. If omitted, protocol's default order is then used, with the most significant bytes coming first in a communication frame, which is called big endian. Please check more information on the specific section about this option, later in this topic.
4.Bit: Allows returning a specific bit of an integer value, which obviously only makes sense in Modbus functions returning integer values or Words. Usually, users are advised to not use this feature, preferring the bit mapping of an application. Bit 1 (one) is the least significant and, the greater the value, the most significant is the bit. The maximum allowed value obviously depends on the size of a data type. The maximum size is currently 64 for Double data types. This field corresponds to the old Use bit mask option on numerical configuration. Please check more information about this option on topic Operations Tab.
Modbus protocol's functions 20 and 21, which access files, use a slightly different syntax from the one described previously:
fr<file>.<register>[.<type>[<size of type>]][.<byte order>][/bit]
Example:
•Device: "" (empty String)
•Item: "1:fr4.101" (reading register 101 from file 4 on Slave Id 1)
Specifically for the special GenSOE function (Elipse Generic SOE):
elsoe<N>.<initial addr.>[.<type>[<size of type>]][.<byte order>][/bit]
Specifically for the special SP SOE function (Sepam SOE), to read all events:
spsoe<type of event>.<initial addr.>[.<type>][.<byte order>][/bit]
Specifically for the special SP SOE function (Sepam SOE), to read events from specific points:
ptspsoe<type of event>.<event addr.>
Specifically for the special GE SOE function (GE PAC RX7 SOE):
gesoe<type of tag + index of point>.<base addr. of queue>
Please check specific topics about the special functions mentioned previously for more information about configuring the respective Tags using Strings.
Instead of explicitly defining Modbus functions or special reading and writing functions to use, as performed on the old numerical configuration and its concept of operations, when configuring using Strings, users define an addressing space through mnemonics listed on the next table, already linked to protocol's pre-defined functions and their respective native data types.
Addressing spaces and mnemonics
Addressing Space |
Mnemonic |
Native Data Type |
Function |
Comments |
Holding Register |
hr |
Word (16-bit) |
Functions 03 and 16 |
Functions 03 and 16 are protocol's most used ones (Modbus class 0) |
Single Holding Register |
shr |
Word (16-bit) |
Functions 03 and 06 |
Function 06 writes to the same registers of function 16, the difference is that function 16 can only write in Blocks, while function 06 writes to a single register at a time, but with less overhead |
Coil |
cl |
Bit |
Functions 01 and 15 |
Single Coil |
scl |
Bit |
Functions 01 and 05 |
Function 05 writes to the same registers of function 15, but cannot write in Blocks, therefore with less overhead |
Discrete Input |
di |
Bit |
Functions 02 and None, read-only |
Input Register |
ir |
Word (16-bit) |
Functions 04 and None, read-only |
Exception Status |
es |
Byte |
Functions 07 and None, read-only |
File Register |
fr |
Word (16-bit) |
Functions 20 and 21 |
abbmge |
Word (16-bit) |
Functions 65 03 and None, read-only |
abbmge.rst |
Not used |
Functions None for reading and 65 01 for writing |
abbmge.rstmxmn |
Not used |
Functions None for reading and 65 02 for writing |
gesoe |
Functions GE SOE for reading and None for writing |
spsoe |
Functions SP SOE for reading and None for writing |
Collects from a meter and returns a structure, with type SP_events, to a Tag with events from any points. For more information, please check topic SEPAM SOE |
ptspsoe |
Int32 |
Collects from a meter and returns to a Tag an integer value from the Edge field, relative to events from a specific point. For more information, please check topic SEPAM SOE |
elsoe |
Word (16-bit) |
Functions GEN SOE for reading, Modbus function 03 with additional algorithms, and 16 for writing |
The table on the previous section lists all protocol's native data types, according to the Modbus functions used, as well as some specific data types used in protocol's non-standard special functions. For Tags returning these native data types, the Data Type parameter can be omitted from the Item field's String.
If users must interpret native data in a different way, which is common among devices using Modbus, they must specify a data type to use, as explained in this section.
A list with all native data types supported by this Driver, as well as their description, can be checked on topic Supported Data Types.
The next table lists all mnemonics used in the <type> parameter of the Item field for each supported data type, Driver-native, and also an alias or an alternative name.
Supported data types
Type |
Mnemonic |
Alias |
Char |
char |
ch |
Byte |
byte |
by or u8 |
Int8 |
int8 |
i8 |
Int16 |
int16 |
i16 |
Int32 |
int32 |
i32 |
Word or UInt |
word |
u16 |
DWord or ULong |
dword |
u32 |
Float |
float |
f |
Float_GE |
float_GE |
fge |
Double or Real |
double |
d |
Int52 |
int52 |
i52 |
UInt52 |
uint52 |
u52 |
String |
string |
s |
Str_I64 |
str_i64 |
s_i64 |
Str_U64 |
str_u64 |
s_u64 |
BCD |
bcd |
GenTime |
gtm |
Sp_time |
Sp_time |
sptm |
UTC64d |
UTC64d |
UTC32 |
UTC32 |
In addition to the data types listed on the previous table, users can also provide mnemonics for user-defined data types or structures. For more information, please check topic User-Defined Data Types.
To use user-defined data types in the Item field, however, the names of these data types must not be case-insensitive, as the Item field does not differentiate upper and lower case. If that happens, this Driver does not allow using these data types in the Item field. For more information, please check topic User-Defined Data Types.
1.Reading or writing Holding Registers, functions 03 and 16, to or from address 100 of a device with Slave Id 1 (one), interpreted as a DWord, with Slave Id in the Device field:
a.Device: "1:"
b.Item: "hr100.u32" or "hr100.dword", or if it is convenient to use a hexadecimal, "hr&h64.u32"
2.Reading or writing Holding Registers, functions 03 and 16, to or from address 150 of a device with Slave Id 3 (three), interpreted as a Float, with Slave Id in the Item field:
b.Item: "3:hr150.f" or "3:hr150.float", or if it is convenient to use a hexadecimal, "3:hr&h96.f"
3.Reading or writing Holding Registers, functions 03 and 16, to or from address 1500 of a device with Slave Id 5 (five), interpreted as a Double, with Slave Id in the Item field:
b.Item: "5:hr1500.d" or "5:hr1500.double", or if it is convenient to use a hexadecimal, "5:hr&h5DC.d"
4.Reading or writing Holding Registers, functions 03 and 06, to or from address 100 of a device with Slave Id 5 (five), interpreted as a Word, with Slave Id in the Item field:
b.Item: "5:shr100" or "5:shr100.u16", or "5:shr100.word". Notice that, because it is a Word, Modbus protocol's native data type for Holding Registers, the data type can be omitted
5.Reading or writing Holding Registers, functions 03 and 06, to or from address 100 of a device with Slave Id 5 (five), interpreted as a user-defined data type named "mytype", with Slave Id in the Item field:
b.Item: "5:shr100.mytype"
NOTE |
The addressing space of Holding Registers in Modbus protocol contains 16-bit registers. Therefore, to read 32-bit data types, such as a DWord or a Float, users must read two "hr" addresses for each Tag accessed. Likewise, reading a Double-type Tag demands the reading of 4 (four) Holding Register addresses. For the same reasons, reading and writing "hr" Tags with a Byte data type can only be performed in pairs. On a device, each Holding Register address always contains 2 (two) bytes. |
BCD and String data types, as they have a variable size, require specifying the size of a data type, in bytes, right after their data type.
Notice that only data types 2 (two) and 4 (four) are valid, that is, 2 (two) and 4 (four) bytes or 4 (four) and 8 (eight) digits for BCD data types. Examples:
1.Reading or writing Holding Registers, functions 03 and 16, to or from address 100 of a device with Slave Id 1 (one), interpreted as a 10-byte-String, or 5 (five) "hr" registers, with Slave Id in the Device field:
a.Device: "1:"
b.Item: "hr100.s10"
2.Reading or writing Holding Registers, functions 03 and 16, to or from address 100 of a device with Slave Id 1 (one), interpreted as a BCD with 8 (eight) digits, or 4 (four) bytes, or 2 (two) "hr" registers, with Slave Id in the Item field:
b.Item: "1:hr100.bcd4"
As explained on the syntax of the previous section, users can add an optional byte order parameter in a Tag's Item field to specify a byte ordering for devices that do not comply with protocol's standard. If a device complies with Modbus protocol's default ordering, this field can be omitted.
If distorted values are read, which can be observed on early tests with a device, and if these values, converted to hexadecimal, are correct after inverting the position of some bytes, please read this section carefully.
The Modbus protocol uses the big endian format by default, where values are formatted with their most significant bytes coming first in communication frames. This is the default format used by this Driver. There is, however, a large amount of devices in the market that use values with other combinations for byte ordering.
As an example, if this Driver reads a value equal to "1234h", or "4660" in decimal, by default this Driver waits that data to be sent with a byte sequence equal to 12h and 34h. If a device uses an inverted default, which is called little endian, then the byte 34h is sent first and then the byte 12h, and this Driver may interpret it as 3412h, or 13330 in decimal, unless these 2 (two) bytes were inverted before interpreting.
For 32-bit values, there are cases when Word values are swapped, but with bytes inside Word values keeping their default ordering. For example, the value 12345678h can be received as 56781234h. There are also other situations, with several different combinations for ordering.
To allow communication with these devices that do not follow protocol's standard byte order, this Driver allows users to configure Tags by specifying the standard to use.
The byte order parameter corresponds to the swap options from the old numerical configuration, and it may have values "b0", "b1", "b2", "b3", "b4", "b5", "b6", "b7", "alias", or else "alias2". For more information, please check the next table.
If the byte order parameter is omitted, data is interpreted as protocol's default, which is equivalent to the "b0" code.
The next table indicates that swap operations, Swap Bytes, Swap Words, and Swap DWords, are performed for each ordering mnemonic, from "b0" to "b7".
Swapping operations
Swap Bytes |
Swap Words |
Swap DWords |
Alias |
Alias 2 (Swaps) |
Order |
b0 |
msb |
by7 by6 by5 by4 by3 by2 by1 by0 |
b1 |
X |
sb |
by6 by7 by4 by5 by2 by3 by0 by1 |
b2 |
X |
sw |
by5 by4 by7 by6 by1 by0 by3 by2 |
b3 |
X |
X |
sb.sw |
by4 by5 by6 by7 by0 by1 by2 by3 |
b4 |
X |
sdw |
by3 by2 by1 by0 by7 by6 by5 by4 |
b5 |
X |
X |
sb.sdw |
by2 by3 by0 by1 by6 by7 by4 by5 |
b6 |
X |
X |
sw.sdw |
by1 by0 by3 by2 by5 by4 by7 by6 |
b7 |
X |
X |
X |
lsb |
sb.sw.sdw |
by0 by1 by2 by3 by4 by5 by6 by7 |
NOTE |
The Order column corresponds to 64 bits, in which b0 is the least significant byte (lsb) and b7 is the most significant byte (msb). |
That is, "b0" does not perform any swap operation on data bytes, keeping the original order of bytes received from a device, which is equivalent to deselecting the swap options on the Operations tab from the old numerical configuration.
The "b1" order, on the other hand, performs a byte swapping, two by two, that is, when receiving a Word, an unsigned 16-bit integer, with the hexadecimal value 0102h, the value returned to a Tag is 0201h, with its bytes swapped. It is equivalent to the old Swap Bytes option.
The "b2" order, on the other hand, performs a swapping of Words, that is, bytes two by two, which obviously affects only 32-bit data or larger. This is the same as selecting the Swap Words option from the old numerical configuration. As an example, if the value 01020304h is received from a device, the value used for application Tags is 03040102h.
The "b3" order, on the other hand, performs a swapping of bytes and Words, which is equivalent to the old Swap Bytes and Swap Words options enabled simultaneously. In this case, the value 01020304h becomes 04030201h.
Likewise, the "b4" order performs a swapping of DWords for 64-bit values, which corresponds to the Swap DWords option from the old numerical configuration, that is, the value 1122334455667788h is interpreted as 5566778811223344h, and so on for all other codes.
The Alias and Alias 2 (swaps) columns specify aliases that users can use for readability, that is, instead of using a "b0" code, users can use an "sw.sdw" alias, and so on.
In most cases, a device's documentation specifies the byte order used, or how to configure it, because there are devices that allow that configuration.
In cases in which a device's documentation does not contain a configuration, users must contact manufacturer's technical support.
If there is no reliable information, users must perform empirical tests, analyzing the returned values, in hexadecimal, comparing them to the expected values, and then observing if there are byte order inversions that may explain the differences.
There are basically the following situations:
1.For devices providing data using Modbus protocol's default byte order, big endian or Motorola, with the most significant bytes coming first, users must omit this parameter or define it as "b0". This is the most common situation.
2.For devices using another standard for byte order, with the least significant bytes coming first, little endian, users must enable all swap options referring to the data type used, which corresponds to the "b7" mnemonic.
3.In the least common case, there are devices that use different byte orders for different data sizes, providing for instance the most significant byte of each Word first, but the least significant Word of each DWord first. Therefore, users must evaluate in which case each swap option must be enabled, thus converting the value returned by a device to protocol's default big endian format.
NOTE |
All mentioned swap options have no effect for Bit data types or data types with a size of 8 (eight) bits, such as Byte, Char, and Int8. Swapping occurs inside each data type, that is, the Swap Words option has no effect for 16-bit data types, as well as the Swap DWords option has no effect for 32-bit data types. BCD data types do not allow swapping operations either. |
The topic Frequently Asked Questions lists a few known cases, already observed on technical supports. Examples:
1.Reading or writing Holding Registers, functions 03 and 16, to or from address 1500 of a device with Slave Id 5 (five), interpreted as a Double without byte inversion, with Slave Id in the Item field:
b.Item: "5:hr1500.d" or "5:hr1500.double", or else "5:hr1500.d.b0"
2.Reading or writing Holding Registers, functions 03 and 16, to or from address 1500 of a device with Slave Id 5 (five), interpreted as a Double with the least significant byte of each Word coming first, and with Slave Id in the Item field:
b.Item: "5:hr1500.d.b1" or "5:hr1500.double.b1", or else "5:hr1500.double.sb"
3.Reading or writing Holding Registers, functions 03 and 16, to or from address 1500 of a device with Slave Id 5 (five), interpreted as a Double with the least significant byte coming first, or little endian, and with Slave Id in the Item field:
b.Item: "5:hr1500.d.b7" or other variations, such as "5:hr1500.d.lsb" and "5:hr1500.d.sb.sw.sdw"
In addition to all Tags described previously, users can configure this Driver's Special Tags using Strings, which are described in details on their specific topics. Please click an item for more information.
Special Tags
Device |
Item |
Operation |
Write-only |
<slave id>: |
Reading or writing |
<slave id>: |
Read-only |