Addressing Tips (Modbus Convention) |
On topic Configuring an I/O Tag, Tag addressing, that is, N4/B4 parameters on numerical configuration, is described based on the most recent Modbus protocol specification, version 1.1b. However, there are devices that still use the old offset addressing convention known as Modbus Convention, which adds offsets to an address. This topic explains how to address Tags if a device's register mapping still follows that old convention, originated from initial Modicon specification, not included on the current specification.
The address provided in the Tag is sent together with protocol's request frame, with or without the default offset of 1 (one), required by the Modbus Data Model specified by the protocol, according to the configuration in the Data Model Offset option, on the Modbus tab of this Driver's configuration window.
In addition to this default offset of 1 (one), defined on the current Modbus standard, version 1.1b, some manufacturers still use the old Modicon standard, known as Modbus Convention, with an offset that can be added to the address, and whose value depends on the Modbus function used, or more specifically, depends on which addressing space this function accessed originally. Such additional offset must be ignored when defining Tag addresses on this Driver. Later on this Manual there are more examples. The next table lists all offsets used by the Modbus Convention standard.
Modbus Convention standard offsets
Data Type (Standard Data Model) |
Modbus Function |
Offset |
Coils |
01: Read Coils (0x), 05: Write Single Coil (0x), and 15: Write Multiple Coils (0x) |
000000 |
Discrete Inputs |
02: Read Discrete Inputs (1x) |
10000 |
Input Registers |
04: Read Input Registers (3x) |
30000 |
Holding Registers |
03: Read Holding Registers (4x), 06: Write Single Register (4x), and 16: Write Multiple Registers (4x) |
40000 |
File Register (old Extended Memory file) |
20: Read General Reference (6x) and 21: Write General Reference (6x) |
60000 |
If a device's register map uses this convention, users must follow this procedure to determine the addresses to attribute to Tags, in the Item field when configuring by Strings or in N4 or B4 parameters for numerical configuration:
1.On the Modbus tab, select the Data is addressed from 1 option.
2.Subtract from the address displayed on device's manual the offset shown on the previous table for the Modbus function used. TIP: Remove the fifth digit from right to the left.
Notice that, in devices that use this old convention, users can determine which Modbus functions can be used to access each register or bit using the offset used in its address.
Examples
Address with Offset (Device) |
Address on I/O Tag (Item or N4/B4) |
Modbus Function |
01234 |
1234 |
01: Read Coils, 05: Write Single Coil, and 15: Write Multiple Coils |
11234 |
1234 |
02: Read Discrete Inputs |
31234 |
1234 |
04: Read Input Registers |
41234 |
1234 |
03: Read Holding Registers, 06: Write Single Register, and 16: Write Multiple Registers |
45789 |
5789 |
65789 |
5789 |
20: Read General Reference and 21: Write General Reference |
Modbus functions 20 and 21 are intended to manipulate reading or writing of multiple subgroups of data, allocated in the equipment's extended memory, or 6XXXXX references, according to the next table.
Extended memory or 6XXXXX references
Memory File Number 1 |
Memory File Number 2 |
Memory File Number 3 |
Register 600100 |
Data 1 |
Register 600200 |
Data 1 |
Register 600300 |
Data 1 |
Register 600101 |
Data 2 |
Register 600201 |
Data 2 |
Register 600301 |
Data 2 |
Register 600102 |
Data 3 |
Register 600202 |
Data 3 |
Register 600302 |
Data 3 |
Register 600103 |
Data 4 |
Register 600203 |
Data 4 |
Register 600303 |
Data 4 |
Register 600104 |
Data 5 |
Register 600204 |
Data 5 |
Register 600304 |
Data 5 |
To use a PLC Tag to read the second register of Memory File Number 2 of Slave ID 1 (one), use the following parameters:
•Numerical Configuration: N1 = 1, N2 = Oper, N3 = 2, N4 = 201
•String Configuration: Item = 1:fr2.201
To use a Block Tag with 3 (three) Elements to read the last three registers of Memory File Number 3 of Slave ID 2 (two), use the following parameters:
•Numerical Configuration: N1 = 2, N2 = Oper, N3 = 3, N4 = 302
•String Configuration: Item = 2:fr3.302
To use a PLC Tag for writing in the fourth register of Memory File Number 1 of Slave ID 3 (three), use the following parameters:
•Numerical Configuration: N1 = 3, N2 = Oper, N3 = 1, N4 = 103
•String Configuration: Item = 3:fr1.103
NOTE |
The Modbus protocol allows users to read or write multiple subgroups (file number) of data through a single request via functions 20 or 21 respectively. However, this Driver only allows users to manipulate one subgroup of data at a time in each PLC or Block Tag. |