I/O Tags |
The N parameters of I/O Tags are not used. Tags are addressed only using the Device and Item parameters.
•Device: Server:LD, configured on the IEC61850 Device Config tab
•Item: LN$Data$DataAttribute or LN$FC$Data$DataAttribute, according to the next table
Available options for the Item parameter
Item |
Operation |
Meaning |
LN$Data$DataAttribute or LN$FC$Data$DataAttribute |
Read or write |
Any Tag to read according to the configuration of Report parameters or polling. If this Tag is for writing, it is accepted by this Driver |
LN$RP$urcbXXXX or LN$RP$bcrbXXXX |
This Driver does not display the tree corresponding to Reports, for simplicity and Tag saving. The whole handling is performed internally. Starting with version 1.0.14, this Driver displays the TimeofEntry Tag (reading and writing) only on Buffered Reports. Starting with version 1.1.18, also displays the EntryID Tag on Buffered Reports |
LN$CO$xxxx or LN$SP$xxxxx |
Write |
Command or control block. To simplify the use of commands, this Driver provides, instead of a tree with the control object, a Block Tag with five Elements, described on the Elements of a command or control block table. The immediate result of accepting or not a command can be retrieved via script, using a Block Tag's WriteEx method on the wWriteStatus parameter, or via status block. Please check the next item for more information |
LN$CO$xxxx$Oper, LN$CO$xxxx$TimeActOper, LN$SP$xxxxx$SBO, LN$CO$xxxx$SBOw, or LN$CO$xxxx$Cancel |
If the Use Single Tag Command Alias option is selected, this Driver creates in Tag Browser a single Tag instead of a Block Tag with five Elements. In this case, sending a command is performed according to section Sending Commands with a Single Tag |
Read |
Command status block. For each block or command Tag a second block is created, with two Elements, that displays the status of operations. This status can be changed as the result of denying to send a command, such as an unsupported command, as the result of accepting, such as a command accepted or not, or as the result of an effective action, such as opening or closing a switch. The first Element of this Block Tag (Status) contains a number code and the second Element (StatusText) contains a textual description of that number code. Please check table Number codes of a command status block for more information |
Element |
Description |
Operation |
Must receive the operation to perform in Text format. Possible values are OPERATE, SELECT, SELECTWITHVALUE, or CANCEL |
Value to send, depending on the type of object, in the CtlVal property |
Time |
Time instant, in Visual Basic standard in days since 1900, for use in a SELECT command by time and filling the T property |
Test |
Indicates whether a command is a test operation (value equal to one) or not (value equal to zero) |
Check |
Type of check performed before performing a command. It must be a number between 0 (zero) and 3 (three) as the result of a logic OR between bits 0: INTERLOCKING and 1: SYNCHROCHECK |
Status |
StatusText |
0 |
Terminated OK |
2 |
Select Accepted |
3 |
Select With Value Accepted |
4 |
Cancel Accepted |
5 |
Operate Accepted |
50 |
Terminate Fail |
100 |
AppError:Unknown |
101 |
AppError:NotSupported |
102 |
AppError:BlockedBySwitchingHierarchy |
103 |
AppError:SelectFailed |
104 |
AppError:InvalidPosition |
105 |
AppError:PositionReached |
106 |
AppError:ParameterChangeInExecution |
107 |
AppError:StepLimit |
108 |
AppError:BlockedByMode |
109 |
AppError:BlockedByProcess |
110 |
AppError:BlockedByInterlocking |
111 |
AppError:BlockedBySynchrocheck |
112 |
AppError:CommandAlreadyInExecution |
113 |
AppError:BlockedByHealth |
114 |
AppError:1_Of_N_Control |
115 |
AppError:AbortionByCancel |
116 |
AppError:TimeLimitOver |
117 |
AppError:AbortionByTrip |
118 |
AppError:ObjectNotSelected |
200 |
WriteError:Object_invalidated |
201 |
WriteError:Hardware_fault |
202 |
WriteError:Temporarily_unavailable |
203 |
WriteError:Object_access_denied |
204 |
WriteError:Object_undefined |
205 |
WriteError:Invalid_address |
206 |
WriteError:Type_unsupported |
207 |
WriteError:Type_inconsistent |
208 |
WriteError:Object_attribute_inconsistent |
209 |
WriteError:Object_access_unsupported |
210 |
WriteError:Object_non_existent |
211 |
WriteError:Object_value_invalid |
212 |
WriteError:Error_unknown |
213 |
WriteError:Timeout |
214 |
WriteError:OutOfMemory |
215 |
WriteError:DecodeError |
216 |
WriteError:WrongParameters |
217 |
WriteError:CmdnotSupported |
•Tag's value is the value used in the CtlVal property
•Tag's timestamp is used in the T property
•The Test property has a fixed value of 0 (zero)
•The Check property has a fixed value of 3 (three, INTERLOCKING and SYNCHROCHECK), except when the N1 parameter is enabled in the option Use Cmd Tag N1 as Check Condition
This operation is defined in the Item property with the Oper (Operate), SBO (Select Before Operate), SBOw (Select Before Operate With Value), or Cancel suffixes.
The Tag for the TimeActivatedOperate operation, with a TimeActOper suffix, is available when the LN contains the OpertTm property. This operation occurs in a way similar to the Operate command, except that the Tag's timestamp is used as the operation's time and a scheduled operation can be canceled using the Cancel Tag.