Configuration by Syntactical Parameters
Reading and Writing
Elipse E3, starting with version 2.0, Elipse Power, and Elipse Water allow configuring Tags by syntactical parameters. Use the next syntax for each field:
•The Device field is not used and it must be kept empty
•The Item field must obey the syntax <Area name><Address>[:<Data type>], in which:
•<Area name> must be filled with a String from table Area Names
•<Address> must be filled with an address value in an Area, or an offset
•<Data type> is optional and, if used, it must be separated by colons and filled with a String from table Data Types. If this data type is omitted, then the default data type for this Area is displayed
Area Names
Area
Meaning
X
Input
DX
Direct input
Y
Output
DY
Direct output
B
Link relay
SB
Special link relay
M
Internal relay
SM
Special internal relay
L
Latch relay
F
Annunciator relay
V
Edge relay
S
Step relay
TS
Timer contact
TC
Timer coil
SS
Integrating timer contact
SC
Integrating timer coil
CS
Counter contact
CC
Counter coil
TN
Timer value
SN
Integrating timer value
CN
Counter value
D
Data register
SD
Special data register
W
Link register
SW
Special link register
R
File register
ZR
File register
Z
Index register
LTS
Long Timer Contact
LTC
Long Timer Coil
LTN
Long Timer Current Value
LSTS
Long Retentive Timer Contact
LSTC
Long Retentive Timer Coil
LSTN
Long Retentive Timer Current Value
LCS
Long Counter Contact
LCC
Long Counter Coil
LCN
Long Counter Current Value
NOTES
•The default data type of Areas TN, SN, CN, D, W, SW, R, ZR, Z, and LSTN is a Word (unsigned 16-bit) and does not accept being configured as a Bit data type.
•The default data type of Areas LTN and LCN is a Double Word (unsigned 32-bit) and does not accept being configured as a Bit data type.
•The default data type of all other Areas is a Bit.
Data Types
Type
Meaning
W or WORD
A Word value (unsigned 16-bit)
S, SH, or SHORT
A Short value (signed 16-bit)
DW or DWORD
A Double Word value (unsigned 32-bit)
L or LONG
A Long value (signed 32-bit)
F or FLOAT
A Floating Point value (32-bit floating point, IEEE 754)
D or DOUBLE
A Double Floating Point value (64-bit double precision floating point, IEEE 754)
BCD
A BCD value (16-bit)
LBCD
A Long BCD value (32-bit)
DATE
A 32-bit value
STR or STRING
A sequence of String characters
The syntax for the Item field, if a String data type is selected, is the following:
•<Area name><Address>:STR[<Maximum length>], in which:
•<Area name> and <Address> refer to the same items from general syntax
•<Maximum length> is optional and informs the maximum size declared in a String. If this size is not informed, then considers the maximum default size of a String as declared on the configuration window of this Driver
NOTE
Only PLC Tags configured for the Data Register, Link Register, or File Register Areas support the String data type. Block Tags or Tags configured with different Areas do not support the String data type.
Examples
1.Reading or writing an Input with address 1 (one) and a basic Bit data type: The Item field is filled with the value "X1".
2.Reading or writing an Output with address 100 and data type configured as Word: The Item field is filled with the value "Y100:W". Values from 16 contiguous Outputs starting at address 100 are reinterpreted as a Word value.
3.Reading or writing a Counter Value with address 50 and a basic Word data type: The Item field is filled with the value "CN50". Filling it with the value "CN50:W" produces the same result.
4.Reading or writing a Data Register with address 1000 and data type configured as Double Word: The Item field is filled with the value "D1000:DW". Values from two contiguous Data Registers starting at address 1000 are reinterpreted as a Double Word value.
5.Reading or writing a Data Register with address 100 and data type configured as String with a maximum size of 64: The Item field is filled with the value "D100:STR[64]".