[N/B] Parameters
[N/B] Parameters
Reading or Writing
N1 or B1
Not used, leave it in 0 (zero)
N2 or B2
Data Type and Area. This value must be composed by the sum of a data type plus an Area. If the value of a data type is equal to 0 (zero), then assumes the basic data type of that Area
N3 or B3
Special usage parameter. Leave it in 0 (zero) if the address in an Area, or offset, is less than 65535 and there is no need to inform the size if a data type is equal to a String. Otherwise, please check topic Using the N3 or B3 Parameter
N4 or B4
Value of the address in an Area, or offset, for values up to 65535. For greater values, please check topic Using the N3 or B3 Parameter
Values for Areas
Value
Meaning
0
Input
1
Direct input
2
Output
3
Direct output
4
Link relay
5
Special link relay
6
Internal relay
7
Special internal relay
8
Latch relay
9
Annunciator relay
10
Edge relay
11
Step relay
12
Timer contact
13
Timer coil
14
Integrating timer contact
15
Integrating timer coil
16
Counter contact
17
Counter coil
18
Timer value
19
Integrating timer value
20
Counter value
21
Data register
22
Special data register
23
Link register
24
Special link register
25
File register
26
File register
27
Index register
28
Long Timer Contact
29
Long Timer Coil
30
Long Timer Current Value
31
Long Retentive Timer Contact
32
Long Retentive Timer Coil
33
Long Retentive Timer Current Value
34
Long Counter Contact
35
Long Counter Coil
36
Long Counter Current Value
NOTES
•The default data type of Areas 18, 19, 20, 21, 23, 24, 25, 26, 27, and 33 is a Word (unsigned 16-bit) and does not accept being configured as a Bit data type.
•The default data type of Areas 30 and 36 is a Double Word (unsigned 32-bit) and does not accept being configured as a Bit data type.
•The default data type of all other Areas is a Bit.
Values for Data Types
Value
Meaning
000
Basic data type of this Area (Bit or Word)
100
Bit (value 1 or 0)
200
Word value (unsigned 16-bit)
300
Short value (signed 16-bit)
400
Double Word value (unsigned 32-bit)
500
Long value (signed 32-bit)
600
Floating Point value (32-bit floating point, IEEE 754)
700
Double Floating Point value (64-bit double precision floating point, IEEE 754)
800
BCD value (16-bit)
900
Long BCD value (32-bit)
1000
32-bit value
1100
Sequence of String characters
NOTE
Only PLC Tags configured for Areas Data Register, Link Register, or File Register support the String data type. Block Tags or Tags configured with different Areas do not support the String data type.
Examples
1.Reading or writing an Input with address 1 (one) and a default Bit data type: The N2 parameter equal to 0 (zero), the N3 parameter equal to 0 (zero), and the N4 parameter equal to 1 (one). If the N2 parameter is equal to "100", then the result is the same.
2.Reading or writing an Output with address 100 and data type configured as Word: The N2 parameter equal to 202, the N3 parameter equal to 0 (zero), and the N4 parameter equal to 100.
3.Reading or writing a Counter Value with address 50 and a default Word data type: The N2 parameter equal to 20, the N3 parameter equal to 0 (zero), and the N4 parameter equal to 50. If the N2 parameter is equal to "220", then the result is the same.
4.Reading or writing a Data Register with address 1000 and data type configured as Double Word: The N2 parameter equal to 421, the N3 parameter equal to 0 (zero), and the N4 parameter equal to 1000. The value from 2 (two) contiguous Data Registers starting at address 1000 is reinterpreted as a Double Word value.