networkPort.fdBbmdAddress
Indicates the BBMD with which the local device is to register as a foreign device when BACnet_IP_Mode is FOREIGN. This property shall be present and writable if BACnet_IP_Mode is FOREIGN.
Property fdBbmdAddress of object networkPort can be read and written using a block tag with 2 elements.
Text Parameters
Property
Value
ParamDevice
<deviceAddress>
ParamItem
networkPort-<objectAddress>.fdBbmdAddress
Size
2 elements
Numeric Parameters
Property
Value
B1:
<deviceAddress>
B2:
<type> = 56
B3:
<objectAddress>
B4:
<property> = 418
Size:
2 elements
Block Elements
Index
Name
Type
0
Host
•A null/empty value.
•A string value representing a sequence of octets, where each octet is represented by a pair of hexadecimal characters (ex: '0F121A').
•A character string containing an XML with a value of type <CharacterString>.
1
Port
A 16-bit integer value ranging from 0 to 65535.