Discrete Alarm

<< Click to Display the Table of Contents >>

 

Discrete Alarm

1.On Substation SE1, Breaker 52-01, select Measurement BreakerPosition on folder Measurements and, using its contextual menu, select the Insert - Discrete Alarm.

Inserting a Discrete Alarm

Inserting a Discrete Alarm

2.Right-click this Discrete Alarm and, on its Properties Window, select the Discrete tab and configure it with the values on the next table.

Configurations of Discrete tab

Name

Message Text

Type

Open

Open

0 - Alarm

Closed

Closed

2 - Return

Intermediate

Intermediate

1 - Event

Invalid

Invalid

1 - Event

 

Discrete Alarm Subconditions

Discrete Alarm Subconditions

3.Execute this application. Change the status of Breaker 52-01 and check if an Alarm appears on the Alarm Summary.

Application at run time

Application at run time

4.Copy this Discrete Alarm from Breaker 52-01 and paste it on Breaker 52-02.

5.Repeat the previous steps to create Alarms for all Switches.

 

CHALLENGE IV

Create an Alarm for the LocalRemote Measurement of all Breakers.