Driver Configuration

<< Click to Display Table of Contents >>

 

Driver Configuration

The [P] configuration parameters of this Driver are not used. All settings are performed on the ME3011 tab of the configuration window, shown on the next figure.

ME3011 tab

ME3011 tab

The available options on this tab are described on the next table.

Available options on the ME3011 tab

Option

Description

Default Slave Address

Default address of a Slave in the network. This value is used if the N1 or B1 parameter of a Tag is equal to 0 (zero)

Update Interval (ms)

Time interval in which this Driver performs a transfer of events from the internal memory to an application. This value must be at least equal to 1000 ms

 

NOTES

•A device is divided internally in up to 4 (four) modules, and each module supports up to 64 digital inputs.

•Internally, this Driver contains a control for the event queue of each module, and it can store up to 1024 events per module.

•Communication with ME3011 Alarm Control Panels is performed using the Serial (RS-485) physical layer.

•The initial configuration of this Driver for serial communication is defined as a 9600 bps baud rate, 8 (eight) data bits, 1 (one) stop bit, and no parity.