Tag Reference
Tag Reference
N1
Address of a device
N2
Command. For more information, please check the next table
N3
Cell or index
N4
Indicates the bit, between 1 (one) and 32, for Tags with the N1 parameter equal to 1 (one) of events that contain bit maps
Available commands on Areva Courier Driver
N2
Operation
Meaning
0
Read-only
Direct reading of cells, or polling. The returned data type depends on the read cell. This command works asynchronously, that is, this Driver internally stores several reading requests and sends a grouped request to a relay, based on the scan time of Tags
1
Read-only
Event reading. If an event belongs to a cell from bit maps, the bit can be informed in the N4 parameter, between 1 (one) and 32. If there is more than one event stored for a cell or bit, then this Driver returns a list of values for each reading
300
Read-only
COMTRADE_WAITING_RECORD. Possible values are 0 (zero) or 1 (one)
301
Read-only
Collecting of a file in COMTRADE format suspended. Possible values are 0 (zero) or 1 (one)
302
Read-only
Status of the internal scan machine relative to each relay
303
Read-only
Active UTR. Possible values are 1: Responding or 0: No response
304
Read-only
Name of the last file in COMTRADE format
305
Read-only
N SCAN OK
306
Read-only
N SCAN NO REPLY
307
Read-only
N SCAN DATA ERROR
308
Read-only
N SCAN SEND ERROR
309
Read-only
N SCAN RETRY
320
Write-only
Saves a file in COMTRADE 1991 format. The available Elements are 1: Command. Possible values are 0: Discards the COMTRADE file, 1: Uses the default name, or 2: Uses the default name plus the date with milliseconds, and 2: Default name
321
Write-only
Default name of a file in COMTRADE format
322
Write-only
Collecting interrupted. Possible values are 1: Asks for an interruption or 0: Cancels an interruption
323
Reading and writing
Slave active or inactive. Possible values are 1: Active or 0: Inactive. Controls any communication from a remote station and must be configured with the value 1 (one) to start communicating
324
Write-only
Time of the last file in COMTRADE format of an application. This command must be written when starting an application to avoid retrieving files already stored. This command is a Block Tag with 7 (seven) Elements. The available Elements are 1: Year with 4 (four) digits, 2: Month, 3: Day, 4: Hour, 5: Minute, 6: Second, and 7: Milliseconds, from 0 (zero) to 999
325
Write-only
Allows informing a link between a number, defined by the formula FUNCTION TYPE × 256 + INFORMATION NUMBER, and a descriptive text. This text is inserted into configuration files to describe the meaning of analog and digital points belonging to a file in COMTRADE format
326
Write-only
Base name of a circuit, for files in COMTRADE format
327
Write-only
Nominal frequency, for files in COMTRADE format
328
Read-only
Number of the current COMTRADE disturbance
329
Read-only
Number of the largest disturbance
330
Write-only
Saves a file in COMTRADE 1999 format. The available Elements are 1: Command. Possible values are 0: Discards the COMTRADE file, 1: Uses the default name, or 2: Uses the default name plus the date with milliseconds, in DDMMYYYY_HHMMSS_000 format, and 2: Default name
340
Read-only
Status byte of a relay. Possible values are 0: If configured, the disturbance records are available for collecting, 1: If configured, changes the Plant Status Word, 2: If configured, changes the Control Status Word, 3: If configured, indicates that a relay is busy, without a possible response withing the time-out period, 4: If configured, indicates that a relay is out of service, 5: If configured, indicates that event records are available for collecting, 6: If configured, changes the LED indicator for alarms, and 7: If configured, changes the LED indicator for tripping
350
Reading and writing
Indicates whether a slave is communicating through the secondary port. Possible values are 1: Secondary port or 0: Main port
351
Write-only
Time of the last event of an application. This time must be written when starting an application to avoid retrieving events already stored. The format of this command is Gregorian or DATETIME
352
Read-only
Time of the last generated file in COMTRADE format, in DATETIME format