Master Profile
Master Profile
Perfil Master
General Driver Configuration
P1
If > 0, it indicates the interval in seconds for the spontaneous sending of date/time, according to the configuration of parameter P2 below (50D0h for PLC and C0D8h for RTU).
P2
If > 0, it indicates that the driver is communicating with a PLC. If = 0, it is a RTU. This setting serves to indicate whether the response to a 51D0h command (time request) is answered with 50D0h (PLC) or C0D8h (RTU).
P3
If > 0, defines the Application Timeout in miliseconds (ex: time to wait for a command execution). If = 0, the default Timeout will be used = 5000 ms. Important: The Timeout parameter, defined at the Setup Tab, defines the channel Keep-Alive, at the datalink layer.
P4
Not Used
General Tag Configuration
N1
BAC Application Address (RTU or PLC). If set to 0 (zero), the tag will use the default value (Rem App Address).
N2
Data Type - see table below
N3
Variable Address
N4
Bit (for commands and digital states)
Tag
Leitura ou Escrita
N2
N3 / COMENTÁRIOS
N4
Analog
Read only
0
Address/Port starting at 0
Not used (let in 0)
Digital State
Read only
1
Bit (0 to 7)
Synchronous Monostable Conmmand
Write only
2
Address/Port starting at 0. In this command, the tag value is not used. The pulse width can optionally be defined in the tag's Item parameter, as follows: W:NNN where NNN is the width in milliseconds. Ex: W:50 (50 milliseconds).
When writing to this tag, no other operation is allowed until a response is received from the equipment (C1D0h) or a timeout occurs.
Bit (0 to 7)
Synchronous Bistable Command
Write only
3
Address/Port starting at 0. In this command, the tag value is used, with 1 to activate and 0 to deactivate.
Bit (0 to 7)
Diagnostics
Read only
5
Diagnostics Byte Index, starting at 0 (zero) up to (total 21 bytes)
Not used
Start Operating Mode Command
Write only
6
Starts RTU operating mode:
Tag Value:
1: Central
2: Local
3: Maintenance
Not used
Finish Operating Mode Command
Write only
7
Finishes RTU operating mode:
Tag Value:
1: Central
2: Local
3: Maintenance
Not used
CPU Hot/Reserve Switchover
Write only
8
Sends the command C0DBh for CPU switchover
Not used
PLC Alarms
Read only
9
Alarm Byte
Not used
Energy Consumption Data
Write only
10
Reserved but not implemented
RDTD - Tariff Registrador
Read only
11
Address starting at 0
Observation: Shall be a block with 4 elements:
Element 0 (TIME): read relative time
Element 1 (DELTA): Sample time in seconds
Element 2 (ACTIVE): Active Energy
Element 3 (REACTIVE): Reactive Energy
Not used
Async monostable Command
Write only
12
Address/Port, starting at 0. The tag value is not used in this command. The pulse width can optionally be defined in the tag's Item parameter, as follows: W:NNN where NNN is the width in milliseconds. Ex: W:50 (50 milliseconds).
When writing to this tag, other operations are permitted, and when a response is received from the equipment (C1D0h) or a timeout occurs, a return tag reading (N2=14) will be triggered.
Bit (0 to 7)
Async Bistable Command
Write only
13
Address/Port, starting at 0. In this command, the tag value is used, with 1 to activate and 0 to deactivate.
When writing to this tag, other operations are permitted, and when a response is received from the equipment (C1D0h) or a timeout occurs, a reading of the return tag (N2=15) will be triggered.
Bit (0 to 7)
Async monostable Command return
Read only
14
Observation: When starting a new command this tag assumes the value BAC_CMD_RESULT_PENDING = 0
When command is finished, this tag will assume one of the values below:
BAC_CMD_RESULT_OK 1
BAC_CMD_RESULT_NOK 2
BAC_CMD_RESULT_CARD_NONEXISTENT 3
BAC_CMD_RESULT_MONITORING_MODE 4
BAC_CMD_RESULT_CENTRAL_MODE 5
BAC_CMD_RESULT_LOCAL_MODE 6
BAC_CMD_RESULT_MAINTENANCE_MODE 7
BAC_CMD_RESULT_TIMEOUT 99
Bit (0 to 7)
Async Bistable Command return
Read only
15
BAC_CMD_RESULT_OK 1
Bit (0 to 7)
ChannelStatus
Read only
17
0 = Primary Channel
1 = Secondary Channel
Tag value is formed by 2 bits, as below:
Bit 0: Channel is Active (Exchanging ACK's)
Bit 1: Channel is in Use (Exchanging Data Messages)
Not used